This article shows practical rules which were developed for the adjustment of Numerical Overcurrent Functions (NOCF) of microprocessor-based protective relays in order to avoid their maloperation due to Transformer Magnetizing Inrush Currents (TMIC). The TMIC waveforms are decaying and nonsinusoidal, and their effects are different on instantaneous, definite-time, or inverse-time NOCF; thus, specific rules are necessary for each type of NOCF. Experimental methods, specifically developed to perform tests of NOCF with TMIC, were applied to four commercial relays from different manufacturers. As each relay has different types of curves, a total of 26 inverse-time curves were included in the set of tests. In practice, the specific behavior of a relay cannot be assumed as known during the coordination of protection; therefore, the rules are based on the worst cases of results (i.e., in order to avoid the incorrect trip of any of the analyzed relays). The input data for the developed rules are the estimated cumulative RMS values of TMIC, assumed as known since there is a long tradition of their estimation. The estimated cumulative RMS values of TMIC, at different time intervals, should be divided by the numerical factors which were specifically proposed for each type of NOCF (to obtain suitable limits to avoid their inappropriate operation). In order to illustrate the application of the proposed rules, the solutions to two cases related to a simple example are shown at the end of this article.