Improving energy efficiency of space heating systems is as important as adopting emerging clean energy technologies for decarbonising heating. While exploring strategies for reducing energy consumption, the space occupants’ expectations to thermal comfort should not be sacrificed. Conventional space heating control systems are often developed under the hypothesis of uniform temperature distribution in a bounded space and the heating system controller is primarily operated based on the information from the temperature sensor at a fixed position. That is, the measured temperature does not represent the temperature surrounding the occupant’s location. This paper explores a new control method; the heating system control is led by the occupant’s thermal experience, expressed by the temperature surrounding the occupant. A new hierarchical state machine control strategy interacting with a Multiphysics simulation model to dynamically estimate the temperature at the point of the occupant is developed. The accuracy of the Multiphysics simulation model is verified based on the corresponding experimental test room data. A co-simulation platform is built to allow COMSOL and SIMULINK to communicate in real-time for control strategy realisation. The experimental results show that the maximum and average mean square error between the measured and simulated temperature under different operating modes is less than 0.21℃ and 0.06℃, respectively. The simulation results indicate that energy consumption could be potentially reduced around 20% with an improved thermal comfort of the occupant by 30%, compared with the conventional fixed sensor control method.