The protection of high voltage alternative current (HVAC) cables is of paramount importance, because conventional distance relays are not capable to precisely determine the fault location. The mutual inductances between core and sheath in HVAC cables as well as significant capacitive effects exert undesirable impact on the seen impedance by distance relays. Thus, in this paper, a new analytical method is proposed for fault location in HVAC cables employing measured voltages and currents at both ends. In the proposed method, the cable is modeled adopting the distributed form of the main parameters. The proposed fault locator searches the entire length of the cable to determine the location of core-to-sheath faults as well as the corresponding fault resistance. To implement the algorithm established in this study, a HVAC underground three-phase single-core cable is simulated in PSCAD/EMTDC environment. Comprehensive simulation studies are conducted by considering different bonding methods, fault resistances and fault locations. Moreover, the performance of the proposed fault locator is evaluated in different operating conditions including noisy environments, source impedance changes, different load levels, high fault resistance, and uncertainties in cable parameters. The results demonstrate that the estimation error does not exceed 1%, which is desirable for practical applications.