This paper demonstrates a practical implementation of a dynamic line rating (DLR) system and an effective ice prediction and prevention method using line monitoring sensors within the FLEXITRANSTORE international project framework. The presented anti-icing system operated continuously for two years. As a part of the project, 4 line monitoring sensors and 2 weather stations were installed on that section of the power line where icing is most likely to occur. These sensors worked continuously and reliably during the demonstration period. The sensor measurements were supplemented with the load value from the SCADA system and weather forecasts, with the help of which, in addition to the real-time line rating and sag-clearance analysis, a predetermined line rating could also be determined. The investigated system also included an ice prediction subsystem as well as a sag-calculation-based ice detection subsystem. Based on the comparison of the measured and calculated parameters, it can be said that both the operation of the sensors and the quality of the data provided by them were satisfactory. In the case of conductor temperature calculation, the developed mathematical models, which can be applied independently, provided information to the system operator with almost similar accuracy than sensors’ measurements. During the observed period, the ice prediction and detection subsystem were also tested and functioned correctly. As an overview of the project, it can be concluded that an efficient DLR-sensor-based anti-icing system is possible to be realized on the high voltage distribution power grid.