This study predicts the long-term performance of ground source heat pump (GSHP) systems in different climatic regions of Japan. The research model calculates the dynamic heat load of a typical Japanese building in various cities using their meteorological data, considering different schedules for heating and cooling seasons. The model aims to analyze the performance degradation of the GSHP system after 15 years of operation due to the imbalanced heating and cooling loads. Additionally, it compares ground temperature changes, coefficient of performance (COP) variations, and annual operation times based on different thermal imbalance ratios (TIR) for the case studies. The results demonstrate that TIR serves as an appropriate factor for comprehensively evaluating system aspects, including GHE length, ground temperature, and COP degradation, across various climates. It was found that ground temperatures increased by a maximum of up to 4 °C in cooling-dominated regions due to higher thermal imbalance accumulative loads, while it decreased to around 1 °C in heating-dominated regions. The model also revealed that the COP decreased in the dominant operation for each case study due to induced thermal imbalance and soil temperature change. The thermal imbalance caused the system cooling COP decreased by 0.015/year in the worst case (Okinawa City) and 0.006/year in average for other cases.
Read full abstract