The thermal performance of a 115 L latent heat storage prototype for cooling data centers was investigated. Experimentally, the heat transfer power and heat absorbed by the heat exchanger during the charging and discharging processes were measured at two flow rates (5 and 10 L/min). Numerically, two phase-change models were developed using the enthalpy and effective heat capacity methods, respectively. The results showed that the enthalpy method provides an overall better prediction of the absorbed heat, whereas the other method only agrees well with the measured results during the melting process. Thus, it is suggested that further modification of the effective heat capacity with temperature improves the agreement between the results. For a volume flow rate of 5 L/min, the average heat transfer power predicted by the enthalpy model was 2290 W during the melting process and > 920 W during the solidification process due to the smaller temperature difference for heat transfer caused by supercooling. The prototype achieved the highest average heat exchange capacity rate when melted to a 50% of its total capacity. This study provides a baseline for predicting and improving the thermal performance of latent heat storage.