To reveal the influence of an over-track-exhaust (OTE) system on particulate matter (PM) concentration and size distribution in underground stations, field measurements were performed at a subway station both in the tunnel ventilation and non-ventilation seasons. By regulating the operating conditions of the OTE system and analyzing different particle size ranges, the characteristics of PM concentration and particulate size distribution under different OTE conditions were obtained. The results show that the normal operation of the OTE system slightly reduces PM concentration, but the effect is negligible. However, it was found that PM concentration increases under long-time operation of the OTE system if the ambient air quality is poor. When the OTE system is operating, the removal efficiencies of particles larger than 2.5 μm are relatively higher. However, the proportion of fine particles (<PM2.5) increases because more fine particles enter the station owing to negative pressure. Correlation analyses of different zones also showed the same result and identified the PM source for each zone. Moreover, the variation trends of the daily average concentration of PM in each zone are in accordance with the ambient environment; thus, the external environment may have a strong influence on subway air quality.