To address the issue of traditional transmission line characteristic parameter testing methods being susceptible to external environmental interference. Proposed a method for processing geographic information data of transmission lines and physical simulation. Firstly, the parameters of the transmission line are tested, a model is established at both ends of the transmission line, and variable frequency signals are collected using 3D GIS technology to develop a lead control box for transmission line parameter testing. Then, the transmission line parameters are calculated online, and real-time voltage and current measurements are conducted at both ends of the transmission line. A zero sequence current simulation diagram of the transmission line is constructed, and circuit parameters are calculated based on the simulation results, Finally, measure the zero sequence parameters of the transmission line using electricity and obtain the zero sequence impedance value of the transmission line using the least squares method. The six zero sequence parameter values were measured in a disturbance environment. The results show that when the power line reaches a certain length, the error of the traditional method has reached 50%, and the testing error of the method studied by the author is less than 3%. The measurement error value of the transmission line characteristic parameter test method based on 3D GIS technology is less than that of the traditional method.