An experimental investigation was undertaken to study the seismic performance of external reinforced concrete (RC) beam-column joints having representative details for mid-rise RC frame buildings in developing countries such as Iran that were designed and constructed prior to the 1970s. Three half-scale external RC beam-column joints were tested by applying lateral cyclic loading of increasing amplitudes. Tested specimens were comprised of one unit having seismic reinforcement detailing in accordance with the seismic requirements of ACI 318-11, and two units having non-seismic reinforcement detailing in accordance with the 1970s construction practice in many developing countries, such as Iran. Two typical defects were considered for the non-seismic units, being the absence of transverse steel hoops and insufficient bond capacity of beam bottom reinforcing bars in the joint region. Test results indicated that the non-seismically detailed specimens had a high rate of strength and stiffness degradation when compared to the seismically detailed specimen, which was attributed primarily to the joint shear failure or bond failure of the beam bottom bars. The non-seismically detailed specimens also showed a 30% reduction in both average strength and ductility and a 60% loss of energy dissipation capacity in comparison to the seismically detailed specimen.