To evaluate the influence of a rigid bus on the interconnected post electrical equipment with a sliding fitting, this article conducted shaking table tests on two full-scaled ±800 kV ultra-high voltage post insulators. Simplifying the rigid bus with a sliding fitting serving as a linear spring and damper allowed us to create a dynamic model of the stand-alone insulators and establish advanced two-piece interconnected post electrical equipment. Later, parametric analyses were carried out on the dynamic model. The results showed that the frequencies of the interconnected system were similar to those of the stand-alone counterparts if the dynamic characteristics of the two interconnected items were similar. The seismic responses of the interconnected system generally decrease compared with those of the stand-alone insulators. Thus, the seismic performance of the rigid bus interconnected electrical equipment system could qualify as having a stand-alone status if the dynamic characteristics of the equipment items are similar. The connection stiffness greatly affects the seismic responses of UHV composite post electrical equipment.