AbstractThe integration of flexible interconnection devices (FIDs) into distribution networks introduces complexities in power flow management under both normal and transient/fault conditions, thereby decreasing the selectivity, sensitivity, and reliability of common current protection schemes. This article examines the impact of FIDs on existing current protection arrangements and proposes a novel method for recalculating the overcurrent protection setting. The AC output characteristics of the FID for a short period after AC fault occurrence are first investigated. It is followed by an analysis of FID's impact on the three‐stage current protection scheme in flexible interconnected distribution networks, conducted through theoretical calculations in MATLAB and simulations in PSCAD/EMTDC. A quantitative assessment of the mal‐operation and non‐operation of current protection caused by FIDs of varying capacities, power flow directions, and locations, with a focus on the typical 10 kV 10MVA FID, is also performed. Based on the above findings, a calculation and modification method for Stage III overcurrent protection setting is presented to address mal‐operation issues in FID‐based distribution networks, with its feasibility validated through electromagnetic transient simulations.