This investigation of the relative merits of various possible transformer connections and protective devices was the result of statistical data secured, over a long period of years, by the Commonwealth Edison Company of Chicago regarding the number and types of distribution transformer failures during lightning storms.* It refers to standard, 60 cycle, overhead, power and lighting distribution systems having 4,000-volt, four-wire primaries and three-wire, 230-volt, three-phase power and 115-230-volt lighting secondary mains. Five spans of standard pole line construction were exposed to transient potentials of steep wave front, the latter being induced by the sudden charging of the well insulated artificial clould suspended over the line. The cloud was charged to potentials, up to 150 kv., by means of a surge generator. Measurements of potentials, ranging as high as 40 kv. in some instances which were induced upon various portions of the distribution system were made by means of ionized sphere gaps and the cathode-ray oscillograph. Some of the important conclusions reached as the result of this investigation are: 1. The value of an experimental wood pole distribution line with an insulated artificial cloud charged by means of a surge generator was definitely established for lightning protective investigations involving induced as well as direct stroke potentials. 2. The practicability and economy of studying, by means of such laboratory equipment, the operation of various transformer, lightning arrester and ground connections, when exposed to surges approximating those of lightning, were demonstrated. 3.