The Rapid Flashover pollution test method (RFO) exposes energized polluted insulators to fog and uses step changes of voltage to identify a minimum flashover voltage. The RFO method reduces test time by a factor of three or more compared to up-and-down voltage application method and is thus time- and cost-effective. In this paper the results from RFO on five ceramic and composite station insulators (line, post and hollow) with median 4.7 m leakage distance are compared closely with duplicate tests using up-anddown procedure. The tests on hydrophobic composite insulators used the preconditioning principles from CIGRE Brochure 555. Full-scale withstand testing of the same five but 420-kV class voltage insulators with median leakage distance 13.3 m are also presented. It is indicated that the flashover test results of RTV-coated station insulators should be specially analyzed and treated.