The purpose of this study was to study the performance of silica gel-air adsorption chiller on two types of adsorber fins by conducting experiments at several cycle times, namely 500, 600, 700 and 800 seconds with specific mass recovery times, heat recovery times, and also variations on the input of the cooling fluid, so that optimal cycle times can be obtained related to COP and SCP. The adsorber fin-spacing which has more tightly fin distance does not determine the better performance of the adsorber for chiller application because the shorter distance of the fin, the cross-sectional area of the silica gel surface that has initial contact with the adsorbate will decrease so that the performance of the adsorber will decrease. The highest cooling capacity and COP obtained are 3.1 kW and 0.52, respectively. The results are obtained on adsorber with 3 mm fin distance and 700 s cycle with hot water inlet temperature of 79°C, cooling water inlet temperature of 29.4°C and chilled water outlet temperatures of 8.5°C