This paper presents the experimental investigation of full-scale precast concrete beam-column connections subjected to cyclic lateral loading. The specimen consists of three models. Two of which are precast beam-column connections and one is monolith. The precast and monolith specimen were designed for the same strength. The cross-sectional dimensions of the beam 250 mm x 300 mm and column 300 mm x 300 mm. Connections are placed in plastic hinge area, with a distance of h (beam height) from the face of the column which is expected to occur first destruction. Precast construction joints are distinguished, with 3 different models, namely monolith, double notch type 1 (STR-1), and double notch type 2 (STR-2). Maximum load capacity, hysterical behavior and energy dissipation are measured, and capacity is compared. The results showed that beam-column joint STR-2 are better able to absorb energy than beam column joint monolith and beam-column joint STR-1. Kumulative energy dissipation of monolith about 9333.07 kN-mm, STR-1 is 8336.76 kN-mm, and STR-2 is 10162.52 kN-mm. The use of dual notch connections (STR-1 and STR-2) provides satisfactory performance, which is marked by meeting the minimum relative energy dissipation ratio at a 3.5% drift according to the ACI Committee 374.1-05. The results show that the STR-2 beam-column connection is more capable of absorbing energy than the monolith beam-column connection and STR-1 beam connection. the value of monolithic cumulative energy dissipation is around 9333.07 kN-mm, STR-1 is 8336.76 kN-mm, and STR-2 is 10162.52 kN-mm. in principle, all three test specimens, monoliths, STR-1 and STR-2 provide satisfactory stability performance under lateral cyclic loads, because they still meet the minimum relative energy dissipation ratio at a deviation of 3.5% according to the ACI Committee 374.1 -05