This paper investigates the temperature rise of vertical/horizontal high-voltage direct current (HVdc) grounding electrodes by simulations and field tests. Based on a field-circuit coupling current distribution model and a three dimensional (3-D) finite element model, a comprehensive methodology is proposed to analyze the transient temperature rise. Since soil resistivity varies with temperature around the electrodes, the temperature-dependent soil resistivity is tested, and then approximated by an empirical formula. Moreover, two practical tests are implemented to validate the simulation model. By ignoring the underground water fluctuations, the calculation results match test results nicely, which demonstrates that the terminal effect of the vertical electrode significantly affects the temperature distribution. But for a horizontal grounding electrode, the current distribution is more uniform than the vertical one. This study provides valuable references for design of HVdc grounding electrodes.