In this study, effect of electrohydrodynamic (EHD) on the condensation heat transfer enhancement and pressure drop of pure R-134a are experimentally investigated. The test section is a 2.5 m long counterflow double tube heat exchanger with refrigerant flowing in the inner tube and cooling water flowing in the annulus. The inner tube is made from smooth horizontal copper tubing of 9.52 mm outer diameter. The electrode is made from stainless steel wire of 1.47 mm diameter. The test runs are performed at average saturated temperatures ranging between 40 and 60°C, mass flux ranging between 200 and 600 kg/m2 s, heat flux ranging between 10 and 20 kW/m2 and applied voltage at 2.5 kV. For the presence of the electrode, the experimental results indicate that the maximum heat transfer enhancement ratio is around 30% while the maximum increase in pressure drop is about 25%.