To address the insufficient collapse resistance of the beam-column welded connection (BWC), this study proposes a strengthening beam-column welded connection with truss elements (BWCTE). A static test on a BWCTE specimen with a composite slab was conducted to investigate its failure pattern, final deflection, and the evolution of axial force, bending moment, and collapse resistance. The results indicate that the addition of truss elements increases the peak load and corresponding deformation of BWCTE by 108.6 % and 27.3 %, respectively, compared to BWC. Moreover, the axial force in the composite beam of the BWCTE specimen achieved the yield axial force, facilitating the complete development of catenary action and optimizing beam performance. Subsequently, primary parameters of the truss element were analyzed using refined numerical models. It is recommended that the projected length of the inside leaning limb is within 0.5 to 0.7 times the height of the steel beam, and the thickness of each limb is within 0.6 to 1.2 times the thickness of the beam flange. Then, the working mechanism of BWCTE was explored through theoretical analysis. The resistance process of BWCTE can be divided into elastic, elastic-plastic, plastic, transition, and catenary stages. The loading and deformation synergies between truss elements and composite beams enable the formation of double plastic zones and double strengthening zones at the beam root, effectively delaying the rupture of the stretched beam flange. Finally, a design method for BWCTE is proposed according to theoretical and numerical analysis.