The fault characteristics of the wind power system, which are reflected in the weak feed features, variation of system impedance, frequency deviation, and non-sinusoidal waveform, will cause the inadaptation of traditional phase selectors to a wind power integration system. In this paper, a new phase selection principle based on the waveform correlation of transient voltage is proposed, which is valid for relay protection of intermittent solar or wind power plants. First, the characteristics of transient voltage of various fault types are deduced according to their boundary conditions. And on this basis, the correlations between the fault transient voltages of every two phases can be acquired. With the differentiated waveform correlations of different fault types, the fault phase selection criterion based on correlation coefficient is formed accordingly. Because it depends on the waveform characteristics of fault transient voltages, the new phase selector is not influenced by the wind power system's fault characteristics and it can select the correct fault phase quickly with high sensitivity. The proposed novel phase selection criterion is verified by the PSCAD-based simulation results and field fault recording data of the wind power integration system.