This study details the experimental investigation of surface condensation heat transfer on vertically inclined aluminium surfaces with simple modifications. A bespoke experimental apparatus was constructed to control the saturation conditions inside the condensation chamber where the test surface is located. The degree of subcooling of the test surface was precisely controlled by an external heat exchanger. The meter bar technique was used to evaluate the condensation heat flux. Using distilled water as the working fluid and a plane aluminium test surface as the baseline case, the experimental apparatus was validated by comparison of the determined heat transfer coefficient with Nusselt’s model of filmwise condensation on a vertical plane surface, where an excellent agreement was obtained. 7 different aluminium test surfaces were subsequently investigated, each one modified with grooves measuring 0.5mm by 0.5mm (height and width), with a consistent spacing of 0.5mm between them. Groove angles relative to the vertical axis of 0° (180°), 30°, 45°, 60°, 90°, 120°, and 150° were investigated, where grooves were symmetrically mirrored at the centre of each test surface. Results highlighted a significant influence of groove angle on the heat transfer coefficient, with the best-performing sample (150˚) producing a maximum enhancement of 45% and an average enhancement of 34% compared to the baseline test surface over the respective range of subcooling.