ABSTRACTAn experimental investigation is presented in this paper on the vapor compression refrigeration cycle used in an ice-making machine with a multi-channel evaporator. To study the operation performance of the refrigeration system in the ice-making machine, the fluid temperature distribution in multi-channel evaporating coils are tested and the dynamic variations in each cooling loop are investigated during the ice-generating phase. The results show that the external cooling loops have the largest temperature fluctuations caused by the large initial refrigerant injecting mass flow and the external environmental disturbances. For the inner cooling loops, the related temperature profiles of different test points have relative stable variations. To reduce the temperature fluctuations of the outside loops, it is suggested to reduce the initial refrigerant mass flow and adjust the initial opening of the thermal expansion valve. Moreover, it is the normal phenomenon for the slight temperature variations for the temperature curves of different test points, caused by the adjustment of thermal expansion valve. During the ice-making process, both the sensible heat removal phase and latent heat removal phase are experienced successively. To remove the sensible heat of water, the refrigerant system is operating in high efficiency with test points having a rapid linear temperature reduction. While for eliminating the latent heat of ice, it requires much more power supply, the relating test points have a temperature decrease with fluctuations. To improve the operation performance of ice machine, some suggestions and improvements are proposed.