Since rail-to-ground insulation decreases, large-level direct currents (DCs) leak from railways and form metro stray currents, corroding the buried metal. To locate the rail-to-ground insulation deterioration area, a location method is proposed based on parameter identification methods and the monitored information including the station rail potentials, currents at the traction power substations (TPSs), and train traction currents and train positions. According to the monitoring information of two adjacent TPSs, the section location model of the metro line is proposed, in which the rail-to-ground conductances of the test section are equivalent to the lumped parameters. Using the rail resistivity and traction currents as the known information, the rail-to-ground conductances are calculated with the least square method (LSM). The rail-to-ground insulation deterioration sections are identified by comparing the calculated conductances with thresholds determined by the standard requirements and section lengths. Then, according to the section location results, a detailed location model of the degradation section is proposed, considering the location distance accuracy. Using the genetic algorithm (GA) to calculate the rail-to-ground conductances, degradation positions are located by comparing the threshold calculated with the standard requirements and location distance accuracy. The location method is verified by comparing the calculation results under different degradation conditions. Moreover, the applications of the proposed method to different degradation lengths and different numbers of degradation sections are analyzed. The results show that the proposed method can locate rail-to-ground insulation deterioration areas.