Integration of wind-based renewable energy sources into long Extra High Voltage/Ultra High Voltage uncompensated/compensated power transmission network poses significant problems in terms of proper detection of power swings and effective discrimination between symmetrical faults and power swing situations. As the existing protection strategies are unable to detect the said circumstances, a novel technique, based on the difference between sending end and receiving end positive sequence currents angles of the transmission line, is proposed in this paper. The required data is collected with the help of Phasor Measurement Units placed on both sides of the line. The scheme results in effective discrimination between distinct faults and circumstances of asymmetrical/symmetrical power swing and achieves satisfactory outcome during current transformer saturation condition. The proposed algorithm is evaluated on the wind-integrated IEEE-9 bus system by producing power swings, various cases of faults, and faults during power swings. Validation of the suggested technique was carried out by the execution of hardware-in-loop simulation on a Real-Time Digital Simulator. The achieved outcomes disclose higher sensitivity and better discriminating ability of the presented technique in comparison with those of numerous prevailing methods.