This study investigates the effects of solar radiation and human metabolic heat due to occupation on the dynamic thermal response of glazed building's floor heating system (FHS), which may entail an indoor thermal discomfort. A full experiment was conducted on a real test cell to measure various parameters such as surface and floor-depth temperature, ambient and operative temperature, and relative humidity. The sun patch was experimentally simulated with a moving heating film placed on the surface of the radiant floor. The performance of the radiant floor was simulated using a TRNSYS® model in conjunction with SketchUp®. Once validated, the model was used to predict the test cell surface, ambient, and operative temperatures under four different scenarios related to the presence or absence of shading and/or occupant gains. Under the realistic climatic data of the city of Troyes (France), the results show that when the solar and occupants gains are considered on the heating slab, the indoor temperature reach the high value of 33.9 °C. A statistical approach based on Design of Experiments (DoE) method was used to perform sensitivity analysis and evaluate the effects of factors/design parameters such as heating pipe thickness, heating slab conductivity, specific heat capacity and density on surface and indoor air temperatures. Findings indicates that heating slab with 6 cm thickness, and with low conductivity and diffusivity leads to better FHS performances with no overheating/discomfort periods. The developed model could serve as a basis for any predictive adaptive control to mitigate the overheating problem.