SummaryIn an attempt to quantify the conductor cable effect on substation electrical equipment, real‐time hybrid simulation (RTHS) is conducted on interconnected equipment using two shaking tables. For this purpose, the existing RTHS system with advanced control capabilities at the Pacific Earthquake Engineering Research Center structural laboratory is enhanced to accommodate the simultaneous use of two shaking tables. An experimental parametric study is conducted to investigate the conductor cable effect using this system with a two‐table RTHS setup. Post insulators of disconnect switches, important components of substations that are usually tested with conventional methods for evaluating their seismic performance, are utilized as experimental substructures for realistic representation of the electrical equipment. Various global and local response parameters, including accelerations, forces, displacements, and strains, are considered to evaluate the effect of the tested conductor cable configuration for a wide range of support structure configurations, which are modeled in the computer as analytical substructures. The experimental parametric study results indicate that the conductor cable has a significant effect on the response of the interconnected equipment over the whole range of investigated support structures and needs to be explicitly considered for seismic testing of electrical equipment. Copyright © 2016 John Wiley & Sons, Ltd.