ABSTRACT This study presents the results of an experimental investigation on the seismic performance of two reinforced concrete coupling beams (CBs) for coupled shear walls, one with a conventional reinforcement layout designed according to the old National Building Code of Canada (NBCC) 1941 and the other one with a diagonal reinforcement configuration designed according to modern NBCC 2015 and Canadian Standard Association (CSA) A23.3 2014 requirements. Experimental tests were conducted to investigate the behavior of specimens under reversed cyclic loading. The experimental results reveal that the diagonal reinforcement configuration could increase the load-resisting capacity and energy dissipation capacity by 4.4 and 10.2 times, respectively. Moreover, the maximum rate of stiffness degradation decreased from 96% in conventionally reinforced CB to 57% in diagonally reinforced CBs. Furthermore, diagonal reinforcement layout led to more stable hysteretic behavior without considerable pinching. In contrast and as expected, the conventionally reinforced CB did not comply with the requirements of the new design code. Therefore, such CBs should be retrofitted to upgrade their seismic performance in conformity with updated standards requirements.