Abstract This paper presents an experimental investigation of local heat transfer characteristics of single-phase flow in a plate heat exchanger (PHE). The local heat transfer coefficient is evaluated using a test section with PHE geometry for measuring wall temperature distribution. The test section of 1.5 mm thickness is employed to consider the heat conduction effect of the heat transfer plate. The results indicated that the local heat transfer coefficient is influenced by the development of the thermal boundary layer along the flow direction and the maldistribution of water flows along both the direction perpendicular to the flow and the stacking direction. The harmonic mean heat transfer coefficient calculated by the measured local heat transfer coefficient agrees with the average heat transfer coefficient evaluated by the modified Wilson plot method within ±25% and within ±16% for the hot side and the cold side, respectively.