An uneven electric field during the operation of an electrode boiler will lead to the emergence of a high field strength area and low field strength area in the furnace, which will endanger the safe and reliable operation and heating efficiency of the electrode boiler. A numerical study of three-dimensional transient electric field distribution characteristics in a 10 kV high-voltage electrode boiler was carried out. The distribution characteristics of the global electric field of the electrode boiler under the nominal voltage of 10 kV were studied, and the distribution law of the electric field of the electrode boiler under poor power quality, such as different bus voltage and three-phase voltage imbalance, was explored. The results show that the electric field distribution characteristics of the three-phase transient are more obvious in the section closer to the electrode disc, and the electric field distribution is the most uniform in the section that is 1.4 m away from the furnace water. In the case of poor power quality, such as different bus voltage and three-phase voltage imbalance, the points of the maximum electric field intensity of the four surfaces change periodically with time, and the greater the bus voltage fluctuation, the more severe the impact on the transient electric field. The three-phase voltage imbalance will shift the peak value of the electric field intensity. The decrease or offset of electric field intensity in the electrode boiler caused by poor power quality will directly affect its heating efficiency. The electric field simulation results have a specific reference value for improving the internal electric field distribution and on-site operation and maintenance of the electrode boiler.