The article considers some aspects of calculating short-circuit currents in mine networks of an underground sec-tion; the shortcomings of traditional methods of calculating short-circuit currents are identified. The article shows that for an accurate calculation, it is necessary to know the actual voltage levels at remote points of the underground section. The influence of the complex resistance of the external power supply network and the ac-tual phase parameter was studied. The article states that the voltage is below the nominal value in the electrically remote connection nodes of the substation's mobile transformers to the underground distribution network and usually no regulating taps are used. The article indicates that according to known methods of calculating short-circuit currents, the voltage on the secondary terminals of the substation transformer is assumed to be equal to the nominal voltage of the network, but in remote areas it is significantly lower and, accordingly, the actual short-circuit currents are 10-12% lower than the calculated ones. It was also investigated that with an increase in the share of the active short-circuit power component, short-circuit currents in district networks increase by 4-5%.