Self-healing or self-assembling power systems that rely on local measurements for decision making can provide significant resilience benefits, but they also must include safeguards that prevent the system from self-assembling into an undesirable configuration. One potential undesirable configuration would be the formation of closed loops for which the system was not designed, a situation that can arise any time that two intentional-island systems can be connected in more than one place, e.g. if tie-line breakers are included in the self-assembling system. This paper discusses the unintentional loop formation problem in self-assembling systems and presents a method for mitigating it. This method involves calculating the correlation or the mean absolute error (MAE) between the two local frequency measurements made on either side of a line relay. The correlation and MAE between these frequencies changes significantly between the loop and non-loop cases, and this difference can be used for loop detection. This paper presents and explains the method in detail, presents evidence that the method's underlying assumptions are valid, and demonstrates in PSCAD two implementations of the method. The paper concludes with a discussion of the strengths and weaknesses of the proposed method.