AbstractInverter‐based distributed generators (IBDGs), mainly solar photovoltaic, connected in medium‐voltage (MV) networks cause challenges, such as voltage limit violations, for distribution network service providers (DNSPs), and require advanced network management strategies to mitigate these challenges. A theoretical analysis of the voltage limit‐induced barrier to IBDG connection and their export limits due to the change in network characteristics is imperative for developing new strategies. The authors formulated a relationship between the network equivalent impedance and the IBDG's connection point in the network and further explored the link between the network equivalent impedance and voltage magnitude due to the IBDG connection point. The authors also assessed the voltage limit‐induced barrier to IBDG connections in MV networks and proposed solutions to overcome issues with the dynamic export limit of IBDGs. Four representative Australian MV networks are analysed in DIgSILENT PowerFactory under different scenarios, such as variation in IBDG location and static and dynamic export limits. The authors found that an IBDG connected at the end of the network can achieve better performance in supporting the network voltage. An IBDG with a dynamic export limit can export three times more energy than the static export limit, which benefits both the DNSPs and IBDG owners.