Reliable and sustainable electrical distribution systems require effective protection measures against internal and external disturbances, especially short-circuit disturbances, to avoid damage to the equipment. Overcurrent relays (OCR) and ground fault relays (GFR) play an important role in the safety of the distribution network. To improve performance, evaluation of relay coordination is essential. During the short circuit, the nearest relay to the fault point is activated first and the backup relay is activated if the fault current exceeds the adjustment of the main relay. Coordination ensures that timely signaling is sent to interrupt the circuit. Inspection of the OCR relay revealed that it did not comply with the IEC 60255 standard and consequently adjusted the classification time to 0.402 seconds. Similarly, the results of the GFR relay inspection did not meet the standards and required an adjustment of the evaluation time to 0.492 seconds. Resolving these deviations is crucial to maintaining the reliability and compliance of the distribution network with industry standards, ensuring that the protection relays respond quickly and effectively to disturbances, thereby preventing possible damage to equipment