Abstract An axial flow cooling fan has been designed for use in a concentrated solar power plant. The plant is based on a supercritical carbon dioxide (sCO2) Brayton cycle, and uses a forced draft air-cooled heat exchanger (ACHE) for cooling. The fan performance has been investigated using both computational fluid dynamics (CFD) and scaled fan tests. This paper presents a CFD model that integrates the fan with the heat exchanger. The objective is to establish a foundation for similar models and to contribute to the development of efficient ACHE units designed for sCO2 power cycles. The finned-tube bundle is simplified, with a Porous Media Model representing the pressure drop through the bundle. Pressure inlet and -outlet boundary conditions are used, meaning the air flowrate is solved based on the fan and tube bundle interaction. The flowrate predicted by the CFD model is 0.5% higher than the analytical prediction, and 3.6% lower than the design value, demonstrating that the assumptions used in the design procedure are reasonable. The plenum height is also found to affect the flowrate, with shorter plenums resulting in higher flow rates and fan efficiencies, and longer plenums resulting in more uniform cooling air flow.