This study assesses the hygrothermal performance of the Photovoltaic External Thermal Insulation Composite System (PV ETICS), using a thick layer of mortar with Phase Change Material (PCM) granules as a passive heat sink. The experimental scenario involved the wall system exposure to real outdoor climate conditions during a 20-month long measurement period. Measured data were compared with results from the hygrothermal modelling. The findings reveal that with carefully designed diffusion channels the PV ETICS demonstrated no accumulation of moisture behind the vapour-tight PV panel. Long term hygrothermal modelling for PCM mortar moisture content with a previously calibrated model predicted stable moisture content around 0.03 m3/m3, significantly lower than the moisture content during first 2 years. Relative humidity behind the PV panel falls into the hygroscopic range on the second spring after the construction. The annual maximum temperatures for PCM mortar during two summers were 69°C, occurring in mid-August. Risk analysis was conducted with historic climate data to understand, whether higher PCM temperatures could be reached in the same climate for different years. Overall, the wall system showed no signs of extensive moisture damage during the testing period, but slight discolouring of the PCM mortar was recorded. This study contributes valuable insights into the practical viability of PV ETICS with PCM mortar, reaffirming its potential for application on larger scale on real building facades.