The harsh environment of the offshore AC network poses challenges to the communication system and the maintenance of the faulty lines, thus the fault location method independent of communication is essential, e.g., non-unit distance protection. However, traditional distance protection is vulnerable to fault resistance and the existing time-domain scheme is affected by the controlled small fault current of converters in offshore AC networks. To emphasize the fault characteristics and improve the performance of protection under fault resistance, the adaptive control of offshore converter is introduced to modulate high-frequency voltage automatically under asymmetrical faults. Based on the high-frequency voltage, the equivalent circuit of the faulty line is established and the derivative equations containing fault distance and transient resistance are deduced. The fault distance is obtained by the improved least-square algorithm and the impact of the small fundamental-frequency fault component is negligible because the high-frequency component is used. In addition, the influence of the fault resistance and the difficulty of near-end fault location are reduced by adopting the improved least-square algorithm, leading to higher reliability. Finally, the effectiveness of the proposed scheme is verified in PSCAD/EMTDC.