High voltage underground cables used in distribution systems provide benefits including aesthetics, reliability, low maintenance costs, and resistance to environmental factors. However, their initial installation expenses are considerably higher than overhead lines, and fault detection is quite challenging. Thus, a deep analysis of dielectric parameters is crucial. Typically, electrical specifications of high voltage underground cables provided by the manufacturer are used for nominal operating conditions. However, it is essential to acknowledge that variations in operational conditions have a discernible impact on the dielectric characteristics of cable insulation. This phenomenon results in an accelerated aging process of the insulation material and contributes to unexpected failures. Hence, it is imperative to determine dielectric parameters of cable insulation under varying operational conditions and elucidate the impact of these operational states on insulation properties. This study involved experimental determination of the dielectric parameters, including capacitance, relative dielectric constant, dielectric loss, and tanδ, for a XLPE insulated high voltage underground cable, designed for a nominal voltage of 12/20 kV. These assessments were performed under varying operating conditions, specifically for distinct voltage, temperature, and frequency. Based on the acquired findings, it is evident that the dielectric characteristics of the cable insulation exhibit substantial variations in response to alterations in voltage, temperature, and frequency, even when operating within the defined nominal limits.