The electric power system must have a protection system with reliable electric power isolation, so that the supply of electrical energy works properly and optimally. There are several kinds of disturbances in the electric power distribution system, one of which is a partial discharge. This study aims to investigate the effect of plate-rod electrodes on partial discharge, partial discharge voltage limits in solid insulation, and the characteristics of partial discharge in electrode media, and waveforms in partial discharge detection sensors. After conducting research, it was found that in the plate-rod type electrode media, the PDIV voltage appeared earlier than the plate-plate electrode media due to the cross-sectional area of the electrode media. And the limit of the pre-discharge voltage of PCB type solid insulation on the plate-bar electrodes is at a voltage of 1.3 kV. Several indicators to determine the characteristics of the partial discharge are background noise off (BGN off), background noise on (BGN on), partial discharge inception voltage (PDIV), and partial discharge voltage. After being examined, the value of each partial discharge detection voltage was obtained at negative and positive polarity voltages on the electrode plates and plate needles respectively 2.85 kV, 2.95 kV and 1.32 kV, 1.57 kV.