To preserve the qualities of the contacts of a circuit breaker, an importantphenomenon to be valued is the arc motion. In this paper, the behaviour of ahigh-current and low-voltage electric break-arc is studied thanks to a meansof diagnostics called `magnetic camera'. One hundred probes measure themagnetic induction outside the breaking device. A processing softwarereconstructs the average line of current representing the arc with a 0.64 µsminimal resolution time, the line being assumed to be composed of segments.The presented study deals with the analysis of a harmful phenomenon for thecircuit breaker: the re-strike during which several arcs exist. Tests havebeen carried out in a quenching chamber composed of a copper or steelsplitting plate with an assumed peak current of 4000 A. One of the maindifficulties of this study taking into consideration the magnetic effects due to steelsplitting plates. Actually, we show that they have a slightinfluence on the location of the line of current.Thanks to the `magnetic camera', the arc positions and their respectiveintensity values are both determined. Besides, differences in behaviour have not beennoticed between the use of a copper and a steel splitting plate.