A simulated system was created to evaluate an air circulation-type geothermal ventilation system, focusing on measuring microbial contamination levels on the surface of the heat exchange unit. Additionally, this study examined sterilization methods using UV lamps on the surface of the heat exchanger. The fungal concentration on the surface of the heat exchanger showed a tendency to increase over time. Although direct comparison is challenging due to the varying concentrations of outdoor air fungi at different measurement times, the surface fungal concentration was highest at a minimum airflow rate of 150 m3/h compared to other conditions. However, since the adhesion of contaminants from outdoor air to the surface of the heat exchanger is influenced not only by airflow but also by outdoor temperature and relative humidity conditions, future research needs to consider these factors. According to the ATP measurement results, microbial contamination was evaluated as “slightly dirty” after 24 h and “dirty” after 48 h of operating the experimental apparatus. Therefore, it is advisable to clean the internal surfaces of the geothermal ventilation system every 1–2 days. The results of the sterilization experiments using UV lamps indicated that irradiation for approximately 30 min inactivated 94.5%-to-96.1% of microorganisms derived from outdoor air. However, since the sterilization dose varies depending on the type of microorganism, it is necessary to determine the optimal irradiation time based on the target microorganisms and the UV lamp’s irradiation intensity.