Electrical apparatuses are prone to arc, which generally causes a fire, even an explosion hazard, when a flammable gas mixture is present, especially during industrial processes. Terrible fire scenes are challenging for fire investigations. In this work, by performing a simultaneous thermal analysis test we simulated a fire environment and found that as the oxygen concentration decreased, the oxidation/exothermic peak temperature of ‘cause’ bead became higher, but the melting temperature was unaffected. Results indicated that the bead pattern underwent oxidation at approximately 831 °C, melting initiated at approximately 1060 °C, and the pattern then disappeared. The melted pattern grain changes were divided into three critical temperature stages: Approximately 600 °C, the onset temperature at which the melted pattern grains began to be equiaxed; approximately 831 °C, at which the grains were interspersed with oxygen-containing material; and 831–1060 °C, when the grains disappeared, which is a criterion for identifying electrical fires. However, the boundaries remained throughout the thermal environment process. Moreover, the bead pattern demonstrated three metallographic regions: Deep layer (Region I), the intermediate layer (Region Ⅱ), and surface layer (Region Ⅲ). Region I was the most thermally sensitive, in which equiaxed crystals first appeared. Region Ⅲ was the thermal reaction lag zone, in which the typical branching crystals finally disappeared, and Region Ⅱ was intermediate between Regions I and Ⅲ. The results may help fire investigators determine the fire scene temperature stages and provide support for fire evidence extraction.