The flow boiling heat transfer characteristics of R290, R600a and their mixtures were experimentally investigated in a horizontal minichannel with an inner diameter of 1.54 mm. In order to investigate the effects of mass flux and vapor quality, heat flux, saturation temperature, and component concentration on the flow boiling heat transfer coefficients, experiments were conducted with mass fluxes ranging from 200 to 400 kg/(m2·s), heat fluxes ranging from 20 to 30 kW/m2, saturation temperatures of 22 °C, 24 °C, and 26 °C, vapor qualities ranging from 0 to 1, and mass ratios of 70/30, 50/50, and 30/70 for R290/R600a. The experimental results indicate that with the increase of vapor quality, the mass flux promotes the heat transfer coefficient more obviously, and the heat transfer coefficient tends to increase first and then decrease. The heat transfer coefficients of both pure and mixed refrigerants increase with increasing the heat flux. The effect of saturation temperature on the heat transfer coefficients of pure and mixed refrigerants is not significant in this study. In the low vapor quality region, the heat transfer coefficients of R290/R600a mixtures are between those of R290 and R600a. As vapor quality increases, the heat transfer coefficients of the mixtures increase more slowly than those of pure refrigerants. In addition, experimental data were compared with the predictions of the empirical correlations. Among all the correlations, the Tran et al. correlation predicts the heat transfer coefficients for R290 and R600a best. The Lim and Kim correlation gives the best predictions of the heat transfer coefficients for R290/R600a mixtures.