• The application of line surge arresters to 150 kV overhead lines is investigated. • The required energy absorption capability of line surge arresters is determined. • Non-gapped line arresters and externally gapped line arresters are compared. • Surge arrester installation configurations are evaluated for critical lines. • Lightning performance improvement of a critical 150 kV overhead line is quantified. This paper investigates the application of Line Surge Arresters (LSAs) to 150 kV double-circuit overhead lines through ATP-EMTP simulations. The 150 kV lines under study are the backbone of the autonomous electrical system of Rhodes island in southeastern Aegean Sea, Greece. Hence, lightning-related insulation flashovers causing outages of these lines may lead to a blackout of this isolated system. In this work, both Non-Gapped Line Arresters (NGLAs) and Externally Gapped Line Arresters (EGLAs) are evaluated. Two installation configurations with 3 and 6 LSAs per tower are considered protecting one circuit and both circuits of the line, respectively. Simulations were performed for both lightning strikes to phase conductors and tower; these may cause shielding failure flashover and backflashover, respectively. The conducted current through the LSAs and the voltage at their terminals are computed, enabling the estimation of the energy stressing the LSAs. The effects of the lightning current time to half value, the phase angle of the operating voltage, and the power frequency ground resistance of towers are assessed. The required LSA energy absorption capability is determined. The lightning performance of a critical overhead line of the Rhodes 150 kV system is estimated and its improvement due to LSA installation is quantified.