The objective of the research is to improve space heating of green buildings by examining experimentally the influence of the heating medium mass flow rate on thermal performance. A green building was built in Cairo, Egypt, that consists of two similar rooms: one is the heated room and the other is a reference for comparison. A photovoltaic thermal (PV/T) collector is used to heat up water in a storage tank, and the hot water in the tank is circulated in the radiant floor of the examined green building. The hot water mass flow rate was varied between 0.04 and 0.08 kg/s. It was found that decreasing the water mass flow rate improves the heating of the radiant floor. The percentage improvement in floor temperature due to heating over the reference room, reaches about 17% and 6% at mass flow rates of 0.04 and 0.08 kg/s, respectively. Engineering Equation Solver (EES) was used to solve the equations for the heat transfer process between the heating water and the floor. It was found that decreasing the mass flow rate increases the residence time of the heating water in the radiant floor, consequently, increases the heat energy transfer and the floor temperature. Increasing the heating fluid mass flow rate in green buildings could have a negative effect on the heat transfer, such that the appropriate heating fluid mass flow rate should be calculated based on the green building massive material as well as the operating conditions, for example, ambient temperature and wind speed.