A micro-gas turbine (MGT) combined cooling, heating and power system coupled with low concentrating photovoltaic/thermal-heat hump (LCPV/T-HP) and absorption chiller is proposed in this study. LCPV/T is used as the heat source of HP to realize mutual promotion. The performance of CCHP system under different operation strategies is dynamically simulated and analyzed by TRNSYS software from energy, exergy, energy-saving, economy and environment. The results demonstrate that both high temperature water source heat pump (HWHP) and low temperature water source heat pump (LWHP) achieved better COP in following electric load (FEL) mode. The average COP of HWHP and LWHP are 22.69% and 4.75% higher than the rated COP, respectively. Annual total cost per unit building area (ATCUBA) and carbon dioxide emissions per unit building area (CDEUBA) are also more advantageous in FEL mode, while primary energy consumption per unit building area (PECUBA), ATCUBA and CDEUBA seems less preferable in following thermal load (FTL) mode. The exergy efficiency and energy efficiency of the system in FEL mode are 19.96% and 41.90% in summer, and 25.13% and 59.36% in winter. Additionally, the equipment with higher exergy loss is mainly LCPV/T, gas-fired boiler, absorption refrigeration unit, MGT and hot water generator under the three operation strategies.