Fire tests were conducted to evaluate the efficacy of incorporating nitrogen to enhance water mist's fire-extinguishing capability in an obstructed, naturally-ventilated 1.22 × 0.61 × 1.22 m high enclosure. Water mist and nitrogen were applied from the enclosure ceiling in the respective ranges of 0.35–3.89 lpm and 0.113–0.283 m3/min, with median droplet sizes ranging from 16 to 35 μm. The obstruction was facilitated with horizontal baffles with various vertical spacings to force the transport of water mist and nitrogen to follow an alternating path to a 76- or 152-mm heptane pan fire sitting on the enclosure floor. The enclosure ventilation was provided with a 0.23 × 0.15 m high base opening centered on the enclosure's front wall, together with a 0.33 × 0.05 m high opening centered on the enclosure's front wall or on the enclosure's back wall at the respective elevations of 0.36 m and 0.81 m above the enclosure floor, or with the presence of these two elevated openings. The tests showed that incorporating nitrogen in the water mist application did improve water mist’ fire-extinguishing capability in the enclosure. However, the improvement was highly affected by the fire size, obstruction and ventilation conditions.
Read full abstract