Abstract In the paper the results of experimental investigations concerning flat slabs made from reinforced lightweight concrete with sintered fly ash aggregate CERTYD were presented. In the research program 6 models made in a natural scale were included. The main variable parameter was slab longitudinal reinforcement ratio. The aim of investigation was the experimental verification of efficiency of double-headed studs as punching shear reinforcement. In the existing technical approvals such kind of reinforcement was allowed only in normal concrete slabs. It was demonstrated that double-headed studs can be an effective transverse reinforcement of lightweight aggregate concrete slabs. The use of double-headed studs resulted in increase in the ultimate load from 19% to 44%, depending on the slab reinforcement ratio which ranged from 0.5% to 1.2%. The comparative analysis showed that the Eurocode 2 provisions were conservative in relation to the experimental results, which were on average 42% higher than the theoretical ones however with a very low 7% coefficient of variation.