The paper discusses the interoperability of the German compensated 110 kV grid and the Polish effectively earthed 110 kV grid. It is assumed that an area of one grid, separated from its power system, will be temporarily supplied from the other grid in its normal regime. Reference is made to the risks associated with phase-to-earth faults in grids so interconnected. Particular attention is paid to the working conditions of surge arresters and voltage transformers in the Polish 110 kV grid deprived of its neutral earthing when supplied from the German grid. DOI: 10.12736/issn.2300-3022.2015211 Background The established cooperation of the Polish National Power System (NPS) with the systems of neighbouring countries takes place at the level of the 220 kV and 400 kV transmission grids, while, for obvious reasons, there have been no interconnections between 110 kV lines. Local cooperation between nearborder 110 kV grid operators can contribute to improved security of supply, and often may be commercially reasonable. When organizing such interoperation, an area of one grid should be prepared, which will be isolated from its own power system and temporarily supplied from the other grid in its normal regime (connected with its power system). The grids will alternate in their supplier/recipient roles. Such interoperation may be relatively easily organised between 110 kV grids with the same neutral earthing modes, and similar standards of power system protections. Such interoperation has been already established, for example between Polish and Czech operators, whose 110 kV grids operate with effectively earthed neutrals. It becomes more complicated when one of the 110 kV grids is effectively earthed, and the other is compensated, as is the case with the neighbouring Polish and German grids. Interoperability analysis of the supply of a separated portion of the Polish 110 kV grid from the compensated German 110 kV grid leads to the following conclusions: • In a fault-free condition, grid interoperation is risk-free. • Given the possibility of short circuits, including phase-toearth faults, no transformer in the separated portion of the Polish grid can have the star point earthed on the 110 kV side. • For the Polish 110 kV grid an earth fault may prove to be dangerous, regardless of its location (in either the Polish or German grid). The overvoltages occurring in these conditions in the healthy phases in the entire grid with coefficient ku = may endanger the Polish grid, which is suitable for overvoltages with coefficient ku ≤ 1.4. • The Polish 110 kV grid protection systems are not suitable to identify and eliminate earth faults in the considered conditions, while the earth faults in the compensated German grid are signalised only by the protection. Ground faults are eliminated through operational activities, with considerable delay. Interoperability analysis of the supply of a separated portion of the German 110 kV grid from the effectively earthed Polish 110 kV grid leads to the following conclusions: • In a fault-free condition, grid interoperation is risk-free. • In the event of phase-to-earth fault in the compensated German grid its earthing and protection systems may prove inadequate for large short-circuit currents. The issue of the interoperability of effectively earthed and compensated 110 kV grids is not new. In the postwar period there was such a need in the Upper Silesian region, and the problem was solved by using a special 110 kV/110 kV coupling transformer. This solution radically eliminates many problems, but has a very significant drawback – it is expensive. It is estimated that for a 160 MVA transformer, the total cost of its building and fitting could amount to approx. 2.5 million EUR. W. Rojewski, M. Sobierajski | Acta Energetica 2/23 (2015) | 114–119