Organic Rankine cycle combined ejector expansion refrigeration cycle (ORC-EERC) has significant potential for utilizing low-temperature heat. The study on dynamic response of the ORC-EERC combined system plays a particularly important role in optimizing the control strategy for the system, given the instability of the low-temperature heat source. In this paper, the ORC-EERC dynamic models with single and dual condensers are proposed. The simulation results show that the proposed improved model of EERC subsystem presents more accurate results relevant to the experiment system. The impact of the ORC subsystem on the refrigeration subsystem is more pronounced in the ORC-EERC system with a single condenser than in the system with dual condensers. In addition, the phenomenon of chocking in the ejector throat leads to the degradation of system performance when the heat source is disturbed. Therefore, a multi-device cooperative control strategy is proposed to enhance the safety and performance of the system. In the case study of geothermal water mass flow scheduling disturbance, the control strategy increases the cooling capacity of the system by a maximum of 9.29%.