The ultra-high voltage direct current (UHVDC) power transmission systems usually transmit a capacity of 6-8 GW, their stability and reliability are of vital importance to the large power grid. This paper analyses a mono-pole blocking accident caused by the inaccurate measurement of optical current transformer (OCT) when the pole line of Shaanbei-Wuhan ±800 kV UHVDC transmission system was struck by lightning. Combined with electromagnetic transient simulation of the UHVDC transmission system, digital simulation and in-plant testing of the optical CT, a comprehensive understanding of the factors contributing to the accident is achieved. It reveals that optical CT measurement anomalies were significant contributors to the misoperation of protective relays, which led to the mono-pole blocking accident. Based on the simulations of optical CT under high peak currents and high di/dt conditions caused by lightning strike, the importance of proper setting of demodulation algorithm parameters in optical CT to avoid inaccurate measurements is emphasized. Through in-plant testing and steady state current accuracy verification, the reasonableness of demodulation parameters is verified. Simulation results illustrate the challenges in measuring very fast transient current accurately, which are the premise and guarantee of stable operation of UHVDC transmission systems under lightning strike.