In the field of hybrid multi-terminal HVdc (high voltage direct current) transmission, an inevitable problem is the short availability of fault information. Namely, only 1-ms complete fault information can be used to identify faults. To overcome this limitation, this study introduces the concept of instantaneous boundary impedance and proposes a dc line protection method. First, a dc transmission line is divided into three types of zones, namely internal, forward-external, and backward-external zones. Then, the instantaneous boundary impedance is analyzed and compared under normal operation and different types of faults. The results indicate that under normal operation, the instantaneous boundary impedance is zero; under a dc line fault, the instantaneous boundary impedance is less than zero; finally, under an external fault, the instantaneous boundary impedance is greater than zero. The proposed principle is validated using Wudongde LCC (line-commuted converter)-VSC (voltage source converter) three-terminal hybrid HVdc RTDS (real-time digital simulation) test system. The experimental results demonstrate that the proposed protection method is effective under different types, locations, and impedances of faults and signal-to-noise ratios within a period of 1 ms. Compared to the existing methods, the proposed protection method can achieve better performance in withstanding fault impedance (600 Ω) and has better robustness against noise interference (10 dB).